Do I need a separate circuit for the FACP in a small office?

Fire · asked 7d ago · 15 views · 3 replies
▲5▼
CS
Crescent Security Original post · 7d ago
Inspector flagged it last time. What's typical?
Follow Report
▲4▼
CW
Coastal Wire GA 6d ago
Ask the AHJ about local amendments, and have the electrician label the panel location on the FACP.
Reply Report
▲4▼
RC
Rocket City Networks Verified company 6d ago
Don't forget the battery calculation; the inspector will usually ask for it too.
Reply Report
▲2▼
KS
Kendall S. Verified company 6d ago
NFPA 72 calls for a dedicated branch circuit with a locked breaker marked FIRE ALARM. Most AHJs enforce it even in small offices.
Reply Report